contactor the L1 L2 T1 7 T3 loction is not the same as the old contactor, when installind new cantactor wich wire go to L1 Lt ect. on new part On single phase your incoming power lines go to L-1 & L-2
...to be on. Technically speaking L1 and L2 stand for Line one and Line two. This would be the incoming power from the breaker or disconnect switch. T1 and T2 are the power leaving the contactor
...T1 and T2 are the power leaving the contactor. All the 220v wires should correspond to one of these four terminals either by screwing them down or fitting the spade connectors together. Usually the ...
...HONEYWELL R8234A CONTACTOR WITH FASCO H140 CONTACTOR? IF SO, WHERE DOES THE L1 AND T1 GO? contactors are just a switch l is the power t is the load (check the coil voltage see that its the same) ...
Question about Central System Air Conditioner
help will be very apreciatred Power leads L1 and L2 to top terminals of contactor. Compressor leads T1 and T2 to bottom terminals of contactor Side terminals get the low voltage leads from transformer
OF THE CONTACTOR. They will make 12vac, 12vdc, 24vac, 24vdc, 120v, 240v, 277v, etc. coils for the contactor. Also keep in mind that when the contactor closes L1 & T1 make contact, L2 & T2, Etc
Question about Mr. Slim MXZ30TN Air Conditioner
...contactor, assuming this is 230 volts, check T1 to T2 should have 230 volts, then check T2 to T3 should have 230 volts then check T1 to T3 should have 230 volts. If you have 230 volts to all 3 wires ...
Question about Mr. Slim MXZ30TN Air Conditioner
contactor (T1 or T2). Start Kit Start from the capacitor to terminal #1 on start relay There should be another wire from here to start on the compressor. Common from contactor ( T1 or T2) to terminal
Question about Mr. Slim MXZ30TN Air Conditioner
...T1 on the contactor to the run cap,from other side of of run cap to T1 on the compressor(start winding?) The parts house told me it does not take a star cap or relay The NEW compressor trys to start ...
...old relay don't say l1 l2 t1 t2 or any indicatio. The contactor should look alike. Just make sure the same wires are on the same side as the old contactor. Don't worry so much of the l1/t1 and ...